Electrical Formulas
Options:
- Motor Formulas
- Transformer Formulas
AC/DC Formulas
To Find Direct AC / 1phase AC / 1phase AC 3 phase
Current 115v or 120v 208,230, or 240v All Voltages
Amps when HP x 746 HP x 746 HP x 746 HP x 746
Horsepower is E x Eff E x Eff X PF E x Eff x PF 1.73 x E x Eff x PF
Known
Amps when kW x 1000 kW x 1000 kW x 1000 kW x 1000
Kilowatts is known E E x PF E x PF 1.73 x E x PF
Amps when kVA x 1000 kVA x 1000 kVA x 1000
kVA is known E E 1.73 x E
Kilowatts IxE I x E x PF I x E x PF I x E x 1.73 PF
1000 1000 1000 1000
Kilovolt-Amps IxE IxE I x E x 1.73
1000 1000 1000
Horsepower I x E x Eff I x E x Eff x I x E x Eff x I x E x Eff x 1.73 x
(output) 746 PF PF PF
746 746 746
2
AC Efficiency and Power Factor Formulas
To Find Single Phase Three Phase
746 x HP 746 x HP
Efficiency
E x I x PF E x I x PF x 1.732
Input Watts Input Watts
Power Factor
VxA E x I x 1.732
Power - DC Circuits
Watts = E xI
Amps = W / E
P = watts
I = amps
R = ohms
E = Volts
3
Motor Formulas
Calculating Motor Speed:
A squirrel cage induction motor is a constant speed device. It cannot operate for
any length of time at speeds below those shown on the nameplate without
danger of burning out.
S rpm = 120 x F
S rpm = 120 x F
P
S rpm = 120 x 60
4
S rpm = 7200
4
S rpm = 1800 rpm
T = 5252 x HP
rpm
4
Example: What is the braking torque of a 60 HP, 240V motor rotating at 1725
rpm?
T = 5252 x HP
rpm
T = 5252 x 60
1725
T = 315,120
1725
T = 182.7 lb-ft
Calculating Work:
Work is applying a force over a distance. Force is any cause that changes the
position, motion, direction, or shape of an object. Work is done when a force
overcomes a resistance. Resistance is any force that tends to hinder the
movement of an object. If an applied force does not cause motion the no work is
produced.
W=FxD
W=FxD
W = 25 x 30
W = 750 -lb
Calculating Torque:
Torque is the force that produces rotation. It causes an object to rotate. Torque
consists of force acting on distance. Torque, like work, is measured is pound-feet
(lb-ft). However, torque, unlike work, may exist even though no movement
occurs.
T=FxD
5
T = torque (in lb-ft)
F = force (in lb)
D = distance (in ft)
T=FxD
T = 60 x 3
T = 180 lb ft
Full-load torque is the torque to produce the rated power at full speed of the
motor. The amount of torque a motor produces at rated power and full speed can
be found by using a horsepower-to-torque conversion chart. When using the
conversion chart, place a straight edge along the two known quantities and read
the unknown quantity on the third line.
T = HP x 5252
rpm
Example: What is the FLT (Full-load torque) of a 30HP motor operating at 1725
rpm?
T = HP x 5252
rpm
T = 30 x 5252
1725
T = 157,560
1725
T = 91.34 lb-ft
Calculating Horsepower:
6
potential difference of 1 volt. It is 1/746 of 1 horsepower. The watt is the base unit
of electrical power. Motor power is rated in horsepower and watts.
Horsepower is used to measure the energy produced by an electric motor while
doing work.
HP = V x I x Eff
746
HP = horsepower
V = voltage
I = current (amps)
Eff. = efficiency
HP = V x I x Eff
746
HP = 230 x 4 x .82
746
HP = 754.4
746
HP = 1 Hp
Horsepower Formulas
Example
To Find Use Formula
Given Find Solution
HP = 240V x 20A x 85%
HP = I X E X Eff.
HP 240V, 20A, 85% Eff. HP 746
746
HP=5.5
I = 10HP x 746
I = HP x 746 10HP, 240V,
I I 240V x 90% x 88%
E X Eff x PF 90% Eff., 88% PF
I = 39 A
To calculate the horsepower of a motor when the speed and torque are
known, apply this formula:
HP = rpm x T(torque)
5252(constant)
Example: What is the horsepower of a 1725 rpm motor with a FLT 3.1 lb-ft?
7
HP = rpm x T
5252
HP = 1725 x 3.1
5252
HP = 5347.5
5252
HP = 1 hp
8
on the other side or a division may be removed from one side of an equation by
making it a multiplier on the other side.
Es x Is Es x Is
A. Ep = B. Ip =
Ip Ep
Ep x Ip
Ep x Ip
C. Is = Es D. Es =
Is
Es x Ip Es x Tp
A. Ep = B. Ts =
Ts Ep
Ep x Ts Ep x Ts
C. Tp = D. Es =
Es Tp
Is x Ts Is x Ts
A. Ip = B. Tp =
Tp Ip
Ip x Tp Ip x Tp
C. Ts = D. Is =
Is Ts
9
Rules Of Thumb"
At 575 volts, a 3-phase motor draws 1 amp per horsepower.
746 watts = 1 HP
Let’s say you have circuit number 27. Divide it by 6. Six will go into 27
four times with a remainder of 3. Normally panels are labeled with the odds
on the left and the evens on the right (see Panel layout example below).
So 3 is the second one down from the top on the odd side, so therefore it
will be "B" phase. Let's try another one; Say your circuit number is 50.
Divide it by 6. Six will go into 50 eight times with a remainder of 2. So the
correct phase for circuit 50 will be "A" phase. This is taken in consideration
if the the 3 phase system is phased A, B, C left to right, top to bottom. This
is the normal phasing of a system.
A - ckt 1 A - ckt 2
B - ckt 3 B - ckt 4
C - ckt 5 C - ckt 6
A - ckt 7 A - ckt 8
B - ckt 9 B - ckt 10
C - ckt 11 C - ckt 12
10
Left Hand Generator Rule:
Thumb = Thrust
Forefinger = Flux
Used to determine the rotation of the armature when the magnetic field polarity of
the pole pieces and the direction of current flow through the armature is known.
The thumb indicates the direction of thrust or movement of the armature. The
forefinger indicates the direction of the field flux assuming that flux lines are in a
direction of north to south, and the center finger indicates the direction of current
flow through the armature.
11
"Three Phase Transformer Info"
Introduction:
12
Figure 1-2: Delta-Wye
connection
Delta Connections:
Figure 1-3:
Wye Connections:
13
In a wye system the voltage between any two wires will always give the
same amount of voltage on a three phase system. However, the voltage
between any one of the phase conductors (X1, X2, and X3) and the neutral
(X0) will be less than the power conductors. For example, if the voltage
between the power conductors of any two phases of a three wire system is
208v, then the voltage from any phase conductor to ground will be 120v.
This is due to the square root of three phase power. In a wye system, the
voltage between any two power conductors will always be 1.732 (which is
the square root of 3) times the voltage between the neutral and any one of
the power phase conductors. The phase-to-ground voltage can be found
by dividing the phase-to-phase voltage by 1.732 (see figure 1-4).
Figure 1-4:
Figure 1-5:
14
Figure 1-6 shows three single phase transformers labeled A, B, and C. The
primary leads of each transformer are labeled H1 and H2 and the secondary
leads are labeled X1 and X2. The schematic diagram of figure 1-5 will be used to
connect the three single phase transformers into a three phase wye-delta
connection as shown in figure 1-7.
Figure 1-6:
Figure 1-7:
15
The primary winding will be tied into a wye connection first. The schematic
in figure 1-5 shows, that the H2 leads of the three primary windings are
connected together, and the H1 lead of each winding is open for
connection to the incoming power line. Notice in figure 1-7 that the H2
leads of the primary windings are connected together, and the H1 lead of
each winding has been connected to the incoming primary power line.
Figure 1-5 shows that the X1 lead of the transformer A is connected to the
X2 lead of transformer c. Notice that this same connection has been made
in figure 1-7. The X1 lead of transformer B is connected to X1, lead of
transformer A, and the X1 lead of transformer B is connected to X2 lead of
transformer A, and the X1 lead of transformer C is connected to X2 lead of
transformer B. The load is connected to the points of the delta connection.
The open delta transformer connection can be made with only two
transformers instead of three (figure 1-8). This connection is often used
when the amount of three phase power needed is not excessive, such as a
small business. It should be noted that the output power of an open delta
connection is only 87% of the rated power of the two transformers. For
example, assume two transformers, each having a capacity of 25 kVA, are
connected in an open delta connection. The total output power of this
connection is 43.5 kVA (50 kVA x 0.87 = 43.5 kVA).
16
Figure 1-8: Open Delta
Connection
Another figure given for this calculation is 58%. This percentage assumes
a closed delta bank containing 3 transformers. If three 25 kVA
transformers were connected to form a closed delta connection, the total
output would be 75 kVA (3 x 25 = 75 kVA). If one of these transformers
were removed and the transformer bank operated as an open delta
connection, the output power would be reduced to 58% of its original
capacity of 75 kVA. The output capacity of the open delta bank is 43.5 kVA
(75 kVA x .58% = 43.5 kVA).
The voltage and current values of an open delta connection are computed
in the same manner as a standard delta-delta connection when three
transformers are employed. The voltage and current rules for a delta
connection must be used when determining line and phase values of
voltage current.
Closing a Delta:
17
Over current Protection for the Primary:
Electrical Code Article 450-3(b) states that each transformer 600 volts,
nominal or less, shall be protected by an individual over current device on
the primary side, rated or set at not more than 125% of the rated primary
current of the transformer. Where the primary current of a transformer is 9
amps or more and 125% of this current does not correspond to a
standard rating of a fuse or nonadjustable circuit breaker, the next higher
standard rating shall be permitted. Where the primary current is less than
9 amps, an over current device rated or set at not more than 167% of the
primary current shall be permitted. Where the primary current is less than
2 amps, an over current device rated or set at not more than 300% shall
be permitted.
Example #1:
What size fuses is needed on the primary side to protect a 3 phase 480v to 208v
112.5 kVA transformer?
* Important when dealing with 3 phase applications always use 1.732 (square
root of 3).
To solve: P / I x E
Since the transformer is more than 9 amps you have to use 125 %.
Answer: 175 amps fuse (the next higher standard, Electrical Code 240-6).
Example #2:
What size breaker is needed on the primary side to protect a 3 phase 208v to
480v 3kVA transformer?
To solve: P / I x E
18
Answer: 15 amp breaker (preferably a 20 amp breaker)
Example:
To solve : P / I x E
19
Single Phase
KVA Amperes
Rating 120V 240V 480V
1 8.33 4.16 2.08
1.5 12.5 6.24 3.12
2 16.66 8.33 4.16
3 25 12.5 6.1
5 41 21 10.4
7.5 62 31 15.6
10 83 42 21
15 124 62 31
25 208 104 52
37.5 312 156 78
50 416 208 104
75 624 312 156
100 830 415 207
167 1390 695 348
200 1660 833 416
Three Phase
KVA Amperes
Rating 208V 240V 480V 600V
3 8.3 7.2 3.6 2.9
6 16.6 14.4 7.2 5.8
9 25.0 21.6 10.8 8.7
15 41.6 36 18 14.4
30 83.0 72 36 28.8
45 125 108 54 43
75 208 180 90 72
112.5 312 270 135 108
150 415 360 180 144
200 554 480 240 192
225 625 540 270 216
300 830 720 360 288
400 1110 960 480 384
500 1380 1200 600 487
750 2080 1800 900 720
20
"3 phase A.C. Motor Windings and Connections:"
21
Two Three Wire Stop-Start Stations:"
22
23
"Hand off Automatic Control:"
24
"Jogging With Control Relay:"
25
DC Motors
Horse-
90v 120v 180v 240v 500v 550v
power
Amperes
1/4 4.0 3.1 2.0 1.6 -- --
1/3 5.2 4.1 2.6 2.0 -- --
1/2 6.8 5.4 3.4 2.7 -- --
3/4 9.6 7.6 4.8 3.8 -- --
1 12.2 9.5 6.1 4.7 -- --
1-1/2 -- 13.2 8.3 6.6 -- --
2 -- 17 10.8 8.5 -- --
3 -- 25 16 12.2 -- --
5 -- 40 27 20 -- --
7-1/2 -- 58 -- 29 13.6 12.2
Horse-
90v 120v 180v 240v 500v 550v
power
Amperes
10 -- 76 -- 38 18 16
15 -- -- -- 38 18 16
20 -- -- -- 55 27 24
25 -- -- -- 89 43 38
30 -- -- -- 106 51 46
40 -- -- -- 140 67 61
Horse-
90v 120v 180v 240v 500v 550v
power
Amperes
50 -- -- -- 173 83 75
60 -- -- -- 206 99 90
75 -- -- -- 255 123 111
100 -- -- -- 341 164 148
125 -- -- -- 425 205 185
150 -- -- -- 506 246 222
200 -- -- -- 675 330 294
26
AC Single Phase Motors
Horse-
115v 200v 208v 230v
power
Amperes
1/6 4.4 2.5 2.4 2.2
1/4 5.8 3.3 3.2 2.9
1/3 7.2 4.1 4.0 3.6
1/2 9.8 5.6 5.4 4.9
3/4 13.8 7.9 7.6 6.9
1 16 9.2 8.8 8.0
1-1/2 20 11.5 11 10
2 24 13.8 13.2 12
3 34 19.6 18.7 17
5 56 32.2 30.8 28
7-1/2 80 46 44 40
10 100 57.5 55 50
Horse-
115v 200v 208v 230v
power
27
15 -- 36 18 14 --
20 -- 47 23 19 --
25 -- 59 29 24 --
30 -- 69 35 28 --
40 -- 90 45 36 --
Horse-
115v 230v 460v 575v 2300v
power
Amperes
50 -- 113 56 45 --
60 -- 133 67 53 14
75 -- 166 83 66 18
100 -- 218 109 87 23
125 -- 270 135 108 28
150 -- 312 156 125 32
200 -- 416 208 167 43
Amperes
1/2 4.4 2.5 2.4 2.2 1.1 0.9 --
3/4 6.4 3.7 3.5 3.2 1.6 1.3 --
1 8.4 4.8 4.6 4.2 2.1 1.7 --
1-1/2 12.0 6.9 6.6 6.0 3.0 2.4 --
2 13.6 7.8 7.5 6.8 3.4 2.7 --
3 -- 11.0 10.6 9.6 4.8 3.9 --
5 -- 17.5 16.7 15.2 7.6 6.1 --
7-1/2 -- 25.3 24.2 22 11 9 --
Horse-
115v 200v 208v 230v 460v 575v 2300v
power
10 -- 32.2 30.8 28 14 11 --
28
15 -- 48.3 46.2 42 21 17 --
20 -- 62.1 59.4 54 27 22 --
25 -- 78.2 74.8 68 34 27 --
30 -- 92 88 80 40 32 --
40 -- 120 114 104 52 41 --
Horse-
115v 200v 208v 230v 460v 575v 2300v
power
50 -- 150 143 130 65 52 --
60 -- 177 169 154 77 62 16
75 -- 221 211 192 96 77 20
100 -- 285 273 248 124 99 26
125 -- 359 343 312 156 125 31
150 -- 414 396 360 180 144 37
200 -- 552 528 480 240 192 49
Horse-
115v 200v 208v 230v 460v 575v 2300v
power
Amperes
250 -- -- -- -- 302 242 60
300 -- -- -- -- 361 289 72
350 -- -- -- -- 414 336 83
400 -- -- -- -- 477 382 95
450 -- -- -- -- 515 412 103
500 -- -- -- -- 590 472 118
29
60 123 61 49 12
75 155 78 62 15
100 202 101 81 20
125 253 126 101 25
150 302 151 121 30
200 400 201 161 40
Horse-
230v 460v 575v 2300v
power
30
31
32
O.S.H.A.
The Occupational Safety and Health Act (OSHA) was legislated to assure,
so far as possible, every working man and woman in the Nation, safe and
healthful working conditions and to preserve our human resources. The
Act applies to business and industry with any number of employs.
The requirements of the Electrical Code, National provide the basis of the
safety provisions of the Act. Specific references to electrical installations
and electrical wiring systems are made in the Electrical Subpart "S".
The Act is "safety oriented", which closely parallels the quality design
characteristics and industrial acceptance of product lines we carry.
We believe that we have a responsibility to assist our customers to meet
the intent of the Act. When and if changes are necessary to ensure the
safety of your electrical systems, we will assist you with proper guidance
and product application information.
33
22. Failure to post job safety and health 53. Respirators not U.S. Bureau of
poster mines approved.
23. Misuse of electrical cords and 54. Faulty cylinder storage
cables
24. Walking and working surfaces
25. Guarding floor and wall openings
and holes
26. Scaffolding, no guard rails
27. Inadequate recordkeeping
Some of these violations are really far fetched, but is is very possible that
one your projects may be visited by an OSHA Inspector. If this happens do
not get excited or upset, do not volunteer any information, but do answer
truthfully any and all the questions asked of you by the inspector.
Inspector has the right to enter and inspect any job site at will.
May inspect OSHA records.
Must present credentials.
Must tell the general scope of the inspection.
At the end of the inspection must advise you as to any and all violations.
34
"Electrical Standards"
This is a list of a few standards in the trade.
PANELBOARDS
Single Phase - 3 Wire Systems
40A | 100A | 150A | 225A |
400A
70A | 125A | 200A | 300A | 600
A
Three Phase - 4 Wire Systems
60A | 150A | 225A | 400A
125A | 200A | 300A | 600A
SWITCHBOARDS
OR
SWITCHGEARS
Single Three
Phase Phase
200 A 400 A
400 A 600 A
600 A 800 A
800 A 1200 A
1200 A 1600 A
1600 A 2000 A
2000 A 2500 A
2500 A 3000 A
3000 A 4000 A
4000 A
35
40 A 125 A 2500 A
450 A
45 A 150 A 3000 A
500 A
50 A 175 A 4000 A
600 A
60 A 200 A 5000 A
700 A
6000 A
For fuses only, additional standard
sizes are 1, 3, 6, and 10.
Disconnects
30A 200A 800A 1600A
60A 400A 1200A 1800A
100a 600A 1400A
36
24" x 18" x
6"
24" x 24" x
6"
24" x 24" x
8"
BUSWAY OR
BUSDUCT
Single Phase Three Phase
225 A 225 A
400 A 400 A
600 A 600 A
800 A 800 A
1000 A 1000 A
1200 A 1200 A
1350 A 1350 A
1600 A 1600 A
2000 A 2000 A
2500 A 2500 A
3000 A 3000 A
4000 A 4000 A
5000 A 5000 A
37
Running Overload Units
38
Motor Branch - Circuit Protective Devices
Maximum Rating or Setting
39
"Power Factor Improvement:"
When using power factor correction capacitors, the total KVAR on the load
side of the motor controller should not exceed the value required to raise
the no-load power factor to unity. Over corrective ness of this value may
cause high transient voltages, currents, and torques that can increase
safety hazards to personnel and possibly damage motor driven equipment.
Diagram
40
60% 1.333 1.004 0.849 0.713 0.583
62% 1.266 0.937 0.782 0.646 0.516
64% 1.201 0.872 0.717 0.581 0.451
66% 1.138 0.809 0.654 0.518 0.388
68% 1.078 0.749 0.594 0.458 0.328
70% 1.020 0.691 0.536 0.400 0.270
72% 0.964 0.635 0.480 0.344 0.214
74% 0.909 0.580 0.425 0.289 0.159
76% 0.855 0.526 0.371 0.235 0.105
78% 0.802 0.473 0.318 0.182 0.052
79% 0.776 0.447 0.292 0.156 0.026
80% 0.750 0.421 0.266 0.130
81% 0.724 0.395 0.240 0.104
82% 0.698 0.369 0.214 0.078
83% 0.672 0.343 0.188 0.052
84% 0.646 0.317 0.162 0.206
85% 0.620 0.291 0.136
86% 0.593 0.264 0.109
87% 0.567 0.238 0.083
89% 0.512 0.183 0.028
90% 0.484 0.155
91% 0.456 0.127
92% 0.426 0.097
93% 0.395 0.066
94% 0.363 0.034
Assume Total plant load is 100
95% 0.329 KW at 60% power factor.
Capacitor KVAR rating
96% 0.292 necessary to improve power
factor to 80% is found by
97% 0.251 multiplying KW (100) by the
multiplier in table (0.583) which
gives KVAR (58.3), nearest
99% 0.143 standard rating (60 KVAR)
should be used.
41
Electrical Formulas
I = amperes
E = volts
KW = Kilowatts
KVA = kilovolt/amperes
HP = horsepower
% Eff. = percent efficiency
PF = power factor
Direct
To Find Single Phase Three Phase
Current
AMPERES when
HP X 746 HP X 746 HP X 746
horsepower is
E X % Eff.X PF E X 1.73 X % Eff. X PF E X % Eff.
known
AMPERES when
KW X 1000 KW X 1000 KW X 1000
kilowatts are
E X PF E X 1.73 X PF E
known
I X E X PF I X E X 1.73 X PF IXE
KILOWATTS
1000 1000 1000
42
2" 344 242 119 141 74 98 367
43
Electrical Conductor Areas
United States
44
240.0 473,760
Electrical formulas for determining amperes,
horsepower, kilowatts and kilovolt-amperes
ALTERNATING CURRENT
DESIRED DIRECT
DATA Two-Phase* CURRENT
Single-Phase Three-Phase
Four-Wire
Amperes when kva x 1000 kva x 1000 kva x 1000 kva x 1000
kva is shown E 2xE 1.73 x E E
Amperes when kw x 1000 kw x 1000 kw x 1000 kw x 1000
kilowatts are E x pf 2 x E x pf 1.73 x E x pf E
shown
Amperes when hp x 746 hp x 746 hp x 746 hp x 746
horsepower is E x %Eff x pf 2 x E x %Eff x pf 1.73 x E x %Eff x pf E x %Eff
shown
Kilovolt- IxE IxEx2 I x E x 1.73 IxE
Amperes 1000 1000 1000 1000
Kilowatts I x E x pf I x E x 2 pf I x E x 1.73 x pf IxE
1000 1000 1000 1000
Horsepower I x E x %Eff x pf I x E x 2 x %Eff x pf I x E x 1.73 x %Eff x pf I x E x %Eff
746 746 746 746
45
The colors brown, red, green, blue, and violet are used as tolerance codes on 5-
band resistors only. All 5-band resistors use a colored tolerance band. The blank
(20%) "band" is only used with the "4-band" code (3 colored bands + a blank
"band").
Example #1
Example #2
46
Example #3
Example #4
Example #5
Example #6
47
CONDUCTOR AND INSULATOR TABLES
48
Copper wire ampacity table
========================================================
| INSULATION TYPE: |
| RUW, T THW, THWN FEP, FEPB |
| TW RUH THHN, XHHW |
========================================================
Size Current Rating Current Rating Current Rating
AWG @ 60 degrees C @ 75 degrees C @ 90 degrees C
========================================================
20 -------- *9 ----------------------------- *12.5
18 -------- *13 ------------------------------ 18
16 -------- *18 ------------------------------ 24
14 --------- 25 ------------- 30 ------------- 35
12 --------- 30 ------------- 35 ------------- 40
10 --------- 40 ------------- 50 ------------- 55
8 ---------- 60 ------------- 70 ------------- 80
6 ---------- 80 ------------- 95 ------------ 105
4 --------- 105 ------------ 125 ------------ 140
2 --------- 140 ------------ 170 ------------ 190
1 --------- 165 ------------ 195 ------------ 220
1/0 ------- 195 ------------ 230 ------------ 260
2/0 ------- 225 ------------ 265 ------------ 300
3/0 ------- 260 ------------ 310 ------------ 350
4/0 ------- 300 ------------ 360 ------------ 405
* = estimated values; normally, wire gages this small are not manufactured with these
insulation types.
49
Silver -------- Element --------------- 9.546 ----------- 1.587-6
50
Dielectric strengths for insulators
Data
51
Motor users and installers get concerned when HOW MUCH UNBALANCE CAN BE
they detect unbalanced phase currents on a 3- TOLERATED?
phase motor. The question is frequently asked:
“Is there something wrong with the motor?” The In general, this depends on the conditions that
other question is: “How much current are found. If the motor is driving the load and
unbalance can be tolerated?” This paper will the highest amperage of the three legs is below
attempt to answer those questions. the nameplate Full Load rating, then generally it
is safe to operate. If the high leg is above the
HISTORY nameplate rating, but within the normal service
factor amps (for a motor with a service factor,
In the “Good Old Days” about the only sources normally 1.15) then it is probably still safe to
of unbalanced phase currents was either a operate the motor. Also, it is not unusual to find
problem in the motor, such as an unbalanced currents more unbalanced at no load than they
number of turns in the windings, an uneven air will be under load, so the loaded amps should
gap or unbalanced phase voltages. Winding or be used. Finally, in general, if the high leg is not
air gap problems are definitely motor related. more than 10% above the average of the three
On the other hand unbalanced phase voltages legs, determined as shown in the example, it is
are a power system problem. Unbalanced probably safe to operate the motor.
voltages will generally produce unbalanced
currents that are many times greater than the EXAMPLE
percentage of voltage unbalance. The ratio
used is close to 8:1. In other words, a voltage Motor Nameplate FLA = 10.0
unbalance of 1% could create unbalanced Service Factor 1.15
phase currents of as much as 8%.
Phase Loaded Amps
A very unscientific way of looking at the
A 10.6
problem is as follows: Suppose a motor has a
nameplate full load current of 10 amps. At full B 9.8
load the amps on each leg of the 3 phases C 10.2
added together would be 10 + 10 + 10 or 30.
However, if the load is the same but the phase Determine the Average
currents are unbalanced, the total of the 3 legs
added together will always be more than the (10.6 + 9.8 + 10.2)/3 = 10.2 amps
total of the balanced currents. In this case the
currents might be 10.5, 11.3 and 12.1 for a total
of 33.9. This is a very unscientific way of Determine the % Difference
looking at it, but it is accurate in describing the
effect. What this means is that high current on (Highest Phase – Average)/Average x 100
one leg doesn’t mean that the other two legs
will be reduced by an equal amount. It can be (10.6 – 10.2)/10.2 x 100 = (.4/10.2) x 100 = .039
said that unbalanced currents always result in x 100 = 3.9%
higher operating temperature, shortened motor
life and efficiency reduction. The following table shows some of the sources
of unbalanced voltages and currents along with
The next question is “What creates unbalanced possible remedies.
currents?” In years past, if the motor was not
the problem — the source of unbalanced
TABLE 1
currents was unbalanced phase voltages.
When measuring line to line voltages from PROBLEM SOLUTION
phase A to B, B to C, and C to A, detectable Blown fuse on a
Search, find and replace
differences in the voltages would show up. The power factor
blown fuse.
voltage differences would account for the correction
unbalanced currents. capacitor bank
Uneven single Locate single phase loads
In today’s world there are other problems that phase loading of and distribute them more
are frequently not detectable with simple the 3 phase evenly on the 3 phase
voltage tests. One problem of growing concern, system circuit.
is voltage distortion caused by harmonics in the Utility unbalanced If the incoming voltages are
52
power system currents. This can happen if voltages substantially unbalanced,
there are loads in the general area that draw especially at lightly loaded
non-linear (harmonic rich) currents from the or no load periods, contact
power system, they can create voltage the utility company and ask
distortion in the normal voltage sine-wave that, them to correct the problem.
in turn, can cause unbalanced currents in Locate the sources of the
motors even when phase voltage differences Harmonic harmonics and use
are not detectable with a voltmeter. For distortion harmonic filters to control or
example, if you were to detect unbalanced reduce harmonics. Install
motor currents and took measurements with a line reactors on existing and
digital voltmeter on the three phases, they new variable frequency
might be very close to one another. The natural controls.
tendency under these conditions would be to
blame the motor for the problem. When this
happens it is necessary to go a step further to SUMMARY
identify or dismiss the motor as the source of
the problem. The test is to rotate all 3 phases. If Unbalanced currents on 3 phase motors are
the power phases are labeled A, B and C and undesirable but a small amount can generally
the motor leads connected to them are labeled be tolerated. Excessive unbalanced currents
1, 2, and 3, motor lead #1 might be can shorten motor life and increase energy
reconnected to power supply lead B; motor lead consumption.
#2 would be reconnected to power supply lead
C, motor lead #3 would be reconnected to
power supply lead A. Moving all three legs will
keep the motor rotating in the same direction.
The currents are recorded on each power line
leg before and after the connections are
changed. If the high current leg stays with the
power line phase (for example, B), then the
problem is a power supply problem rather than
a motor problem. If, however, it moves with the
motor leg, then it is a motor problem. This test
will pinpoint the problem to be either power
supply or motor.
53
STAR DELTA START UP PRINCIPLES
Important that the pause between star contactor switch off and Delta
contactor switch is on correct. This is because Star contactor must be
reliably quenched before Delta contactor is activated. It is also important
that the switch over pause is not too long.
If Star connection has sufficient torque to run up to 75% or %80 of full load
speed, then the motor can be connected in Delta mode.
During transition period of switchover the motor must be free running with
little deceleration. While this is happening "Coasting" it may generate a
voltage of its own, and on connection to the supply this voltage can
randomly add to or subtract from the applied line voltage. This is known as
transient current. Only lasting a few milliseconds it causes voltage surges
and spikes. Known as a changeover transient.
54
Electric Motor Wire Connections
Rotation L1 L2
CCW 1,8 4,5
CW 1,5 4,8
T1 T2 T3 T7 T8 T9
55
Motor Leads 1 2 3 7 8 9
T1 T2 T3 T7 T8 T9
Together
Motor Leads 1 2 3 7 8 9
4&5&6
T1 T2 T3 T7 T8 T9
NEMA 1,6 2,4 3,5 7,12 8,10 9,11
IEC 1 2 3 7 8 9
L1 L2 L3 Join
1 2 3 4&5&6
L1 L2 L3
1,6 2,4 3,5
56
NEMA Nomenclature--9 Leads:
Dual Voltage WYE-Connected
Voltage L1 L2 L3 Join
4&7, 5&8,
High 1 2 3
6&9
Low 1,7 2,8 3,9 4&5&6
Voltage L1 L2 L3 Join
4&7,
High 1 2 3
5&8,6&9
Low 1,6,7 2,4,8 3,5,9 ------------
Voltage L1 L2 L3 Join
4&7, 5&8, 6&9,
High 1 2 3
10&11&12
Low 1,7 2,8 3,9 4&5&6, 10&11&12
Dual Voltage
WYE-Connected Start
Delta-Connected Run
57
mode
Start WYE U1 V1 W1 U2&V2&W2
Run Delta U1,W2 V1,U2 W1,V2 --------------
Typical
Speed L1 L2 L3
Connection
Typical
Speed L1 L2 L3
Connection
58
Typical
Speed L1 L2 L3
Connection
Typical
Speed L1 L2 L3 Connection
1U&1V&1W--
High 2W 2U 2V 2 WYE
JOIN
Low 1U 1V 1W 2U-2V-2W OPEN 1 Delta
Typical
Speed L1 L2 L3 Connection
1U&1V&1W--
High 2W 2U 2V 2 WYE
JOIN
Low 1U 1V 1W 2U-2V-2W OPEN 1 WYE
59
Considerations for the Use of
AC Induction Motors on
Variable Frequency Controllers
in High Performance Applications
Abstract
Until recently the majority of AC variable speed drives have been applied to
variable torque, pump and fan applications. Advances in drive technology have led
to the use of induction motors in high performance applications that exceed the
capability of motors designed for operation on sine wave power. These
applications, which have traditionally been served by DC systems, have created
the need for definite purpose AC induction motors designed specifically for
operation on adjustable frequency controllers. This paper will discuss many of the
considerations for a successful application and will highlight the limitations of
standard motor designs.
Introduction
The reasons for operating industrial motors over a range of speeds are as varied as
the industries served. The need for variable speed prime movers is widespread -
energy savings on fan drives, constant surface speed cutting on machine tool
spindles, wind and unwind operations of a bridle drive, etc. Improved performance
of these variable-speed drive systems has always been a key means for achieving
increased factory productivity. While various methods have historically been used
to achieve these speed ranges, advances in technology are making one of the
options more attractive than ever.
The low cost and ruggedness of the AC squirrel cage induction motor are benefits
which have increased the desire to use it as the electromechanical energy
60
conversion means. Today's control schemes are obtaining higher levels of
performance from these AC motors as well. However, a common limiting
characteristic of AC induction motors' performance (on adjustable frequency
controls) has not been a technological limitation. Rather, it has been a limitation
imposed by the nature of the standardization of industrial AC motors for general-
purpose, constant-frequency use. Throughout this highly refined standardization
process there has been little consideration for operation on variable frequency
power.
Until recently the majority of high performance industrial applications have been
satisfied using DC motors and controls. This technology has well defined
standards and has been dominated by a limited number of manufacturers where the
control supplier assumes responsibility for the performance of the control/motor
system.
When the "drive" (motor and control) performance requirements are minimal, a
standard industrial AC induction motor can often be successfully applied to
adjustable-frequency power, variable-speed applications. Indeed, some
applications can be converted from constant speed to variable speed while
utilizing an existing induction motor. However, when the performance level
required is more demanding, a definite-purpose motor design is appropriate. This
is usually the case when maximum process productivity is the goal.
61
• A process (driven machine) that cannot be started or run without a variable
speed control
The vast majority of adjustable frequency AC controls applied to date have been
on low performance applications such as pumps, fans and mixers. Only recently
have significant numbers been applied to applications such as extruders, winders
and coordinated web processes that meet the criteria above. As improvements in
control technology make these applications commonplace there is a need for
definite purpose motors designed specifically to optimize the performance of the
drive.
General Considerations
The first task is to design a basic motor configuration which is matched to the
general needs of adjustable frequency power and variable speed operation.
Second, the design must be adaptable to match the specific needs of many
different drive applications. Third, by relaxing inappropriate constraints associated
with fixed frequency, fixed voltage, fixed speed applications the design can be
tailored to meet the performance objectives by making typical design tradeoffs as
outlined in Table 1. Also, when the controller design is known, more subtle
techniques which include the controller can be used. An example is the use of a
lower than usual voltage at the low speed end of a region of constant horsepower,
so that the flux level (hence, peak load capability) at the highest speeds can be
maximized to produce sufficient torque without having to oversize the motor. Of
course, this must be weighed against the increased current required of the
controller at the low speed.
62
Lower Flux Density Increase volume of core
Increase stator coil turns
Lower Magnetic Noise Level Decrease slot sizes
Decrease flux density
Alter shape/volume of material
Higher Efficiency Decrease stator resistance
Decrease rotor resistance
Reduce flux density
As can be seen from Table 1, there are many design compromises that can be
made within the motor to provide optimum performance for a given application.
The following paragraphs will discuss issues that are commonly raised in
discussions of variable frequency applications.
Starting Characteristics
Figure 1
Fixed Voltage and Frequency
Speed Torque Curve
63
Figure 2
Overload Torque Per Amp
Peak Currents
In addition to the RMS current level, an important rating point for a transistor
(typically used in adjustable frequency controllers) is the peak current capability.
The high frequency transient current which results from the electronic switching
of the control output voltage is inversely proportional to the leakage inductance of
the motor. As noted in Table 1 the leakage inductances can be increased by
altering the design of the windings and the magnetic cores in the motor. The use of
an electromagnetic design specifically for adjustable frequency power can
significantly reduce the peak current required for a given level of power output
(see Figure 3). This will not only improve the reliability of the drive, but often can
prevent costly over sizing of the AC controller and provide the most cost effective
solution.
Figure 3
Typical PWM Current Waveforms
64
Motor Heating
When an induction motor is run with voltage and current waveforms as seen in
Figures 4a through 4d, the deviation from the ideal sinusoidal wave shapes create
additional losses without contributing to steady state torque production. The
higher frequency components in the voltage waveform do not increase the
fundamental air gap flux rotating at synchronous speed. They do, however, create
secondary "hysteresis loops" in the magnetic steel, which along with high
frequency eddy currents produce additional core losses and raise the effective
saturation level in the lamination material. As another consequence of these higher
frequency flux variations there are higher frequency currents induced in the rotor
bars which generate additional losses. Appropriate electromagnetic design,
including rotor bar shape can minimize these added losses.
The higher frequency components of the current waveform also do not contribute
to the steady state torque. They do, however, increase the total RMS current
resulting in added I R losses in the stator winding. In addition to higher frequency
current components there can also be low frequency "instabilities" in the currents
seen by the AC motors on variable frequency controllers. These asynchronous
components of current again cause added losses without contributing to the steady
state torque production. Motor designs which help minimize harmonic currents
lead to lower I R losses.
65
Typical Waveforms from Adjustable Frequency Controllers
Figure 4A
Voltage at 50% of Base Speed
Figure 4B
Current at 50% of Base Speed
Figure 4C
Voltage Near Base Speed
66
Figure 4D
Current Near Base Speed
Motor Cooling
As has been well documented in the literature, when AC motors are run across a
wide speed range their heat transfer effectiveness will vary a great deal. Cooling
fans whose rotation is directly supplied by the motor are subject to high windage
losses and noise at high speeds. Modern AC controllers are capable of operating
across a very wide frequency range, often up to several hundred hertz. While this
provides great flexibility in the control, it places the motor cooling fan well above
its fixed frequency design operating point which often leads to inefficient air flow
and objectionable noise. In low speed operation the fan's effectiveness falls off
with the motor's speed. Figure 5 shows typical cooling curves for a family of
totally enclosed fan cooled motors. In variable torque applications this reduction in
cooling air often stays in balance with the reduction in motor losses as the load is
reduced with speed. However, in constant torque applications the motor's
temperature limits will likely be exceeded. An independently powered blower can
provide an essentially constant heat transfer rate. Although not a standard fixed
frequency motor feature, depending on the load/speed profile required by the
application, this can be a very effective choice and is often specified for high
performance applications.
67
An offshoot of motor cooling is the need to protect the motor should the motor
cooling system fail. While thermostats and thermistors are not common in fixed
frequency AC motors they should be required for variable speed applications. A
standard AC motor operates at a fixed speed on a well-defined power supply
which allows the shaft driven fan to provide adequate cooling air in all normal
circumstances. By design a variable frequency control will allow the motor to
operate at very low speeds where little or no cooling is provided. This might occur
during maintenance, jog, or threading operation for example. On the other hand, if
a separately powered blower is provided the drive motor must be protected from a
potential blower failure. As is the case with DC motors, over temperature
protection is recommended.
Figure 5
Cooling Curves for TEFC Motors
In applying variable frequency controllers attempts are often made to use either "in
place" AC motors, or standard sine wave power designs. To do this, and operate
across a speed range the motor is often oversized relative to the rating required by
the application. This can sometimes be done successfully, but there are a number
of potential pitfalls. These can range from something as basic as a motor insulation
system which is fine on sine wave power, but inadequate for the voltage and
current wave shapes on the controller, to drive system instability due to a lack of
damping. The oversized motor will have correspondingly higher rotor inertia,
which could lengthen acceleration and deceleration times and reduce process
productivity. Also, since no load current tends to be a fairly constant percentage of
full load current within a motor product line, the higher no load current of a
derated motor could result in lower power factor and higher current at the load
point required by the application. This current may exceed the capability of the
variable frequency controller requiring a costly over sizing of the controller as
well. A derated motor will have a lower nominal slip at the application load than a
matched motor, which can cause problems either with load sharing in the case of
multi-motor drives or with IET trips whenever the load changes quickly. While it
often appears to be economic to oversize a standard motor to achieve a greater
68
speed range, this course of action should be approached cautiously while weighing
all factors of the desired performance of the drive.
As power transistor technology has evolved, there has been a proliferation of variable
frequency controllers operating at an AC input voltage of 460 V, using these transistors
as the power-switching device. As the transistor manufacturers have continued to push
toward devices with lower losses and the capability of the higher switching rates, a result
has been very rapid transition times between the "off" and "on" states. This is the case for
both bipolar (BJT) as well as insulated gate (IGBT) transistors.
The combination of fast transitions (turn-on time) and the DC bus voltages of 460 VAC
(input) controllers results in the high "dV/dt" levels as seen in Figure 6. What is typically
referred to as dV/dt is the time derivative of the voltage, or the slope of the voltage versus
time curve.
Figure 6
Typical Transistors Transistion
Voltage
Increasing the dV/dt levels at the variable frequency controller output (and motor
input) can have effects which need to be considered in the design of motors for
such applications. The significance of these effects can be shown by the following
equation:
I = C x dV/dt
As can be seen from this equation, as dV/dt increases, the capacitively coupled
current increases linearly with it. While items such as lead wires and motors are
not usually thought of in terms of capacitance, three phases AC motor windings
have a capacitance to ground as well as between phases. The leads between the
controller and motor also exhibit similar effects. While these capacitance values
are normally considered negligible, given enough dV/dt, it does not take much "C"
to get quite a bit of "I".
A second way of viewing the high dV/dt levels is to use transmission line theory
to compute the voltage distribution due to the propagation of the steep wave front.
69
This involves careful modeling of the leads and motor windings as well as
transition points such as conduit box connections. Reflected as well as incident
wave fronts must be computed and combined. This type of analysis will not be
described in this paper. Analyses done by this methodology are susceptible to
errors due to many things including the choice of appropriate complex impedance
models for circuit components. Generally, the results of this type of analysis have
indicated that the first length of wire in a motor will see higher voltages than will
subsequent parts of the winding. This type of modeling is typically used for the
analysis of high voltage surges incident on the terminals of very large machinery.
Another result of the very fast transition time of today's transistors is that the
voltage at the inverter output and the motor terminals is not the same. The voltage
wave shapes in Figures 7 and 8 demonstrate typical differences. Using the
transmission line model mentioned above, the two major differences in these wave
shapes can be explained as follows. The impedance of the leads results in the
voltage wave front being distributed to some extent across those leads, softening
the wave front to a lower dV/dt level at the motor terminals. Secondly, the
termination of the transmission line (leads) at the motor results in a reflected wave,
producing the overshoot and dampened oscillation seen in Figure 8. This
waveform could also be modeled as the response of an L, R, C, circuit to an
impulse input.
Figure 7
Voltage Wave front at Inverter Output
Figure 8
Voltage Wave front at Motor Terminals
70
The end result of these wave shapes being applied to the motor terminals is
increased stress on the insulation system. Since these wave shapes do not exist in
sine wave applications it is clear that their effect has not been considered in
standard AC motor insulation systems. The motor insulation system must be
capable of withstanding the increased thermal stress as well as the capacitively
coupled currents and voltage stresses. Appropriate selection of individual
materials, properly integrated into a motor insulation system is needed to
withstand the demands of operation on variable frequency controllers.
While NEMA standards for fixed speed AC motors allow for a 10% voltage
variation from nominal, it is important to recognize that at 10% lower than
nominal flux, performance including the nominal HP rating will vary. For
example, it may require 10% more current than nominal to deliver rated HP.
While this additional current is almost always available from the incoming line it
may not be available from the variable frequency controller. Users that are
familiar with static DC drives and their characteristics in low line conditions may
be unpleasantly surprised to find that AC variable frequency controllers often do
not provide the same rating capability at low line conditions. Operation of an AC
motor at lower than nominal flux levels will result in increased slip and rotor
heating which is self compounding and may lead to a thermal runaway condition.
High efficiency AC motors designed for sine wave operation are often particularly
susceptible to poor performance when the controller output voltage is low, since
they usually employ low flux density designs at nominal terminal conditions.
71
matched) is required. Since voltage isolators typically cannot faithfully reproduce
these wave shapes, the scope must be "floated" unless the variable frequency
controller is operating on a floating power system. This then requires appropriate
care to avoid electrical shock to the operator.
Not only is measuring the voltage pulses difficult, all other measurements on the
equipment are exposed to this high dV/dt environment. This requires the use of
equipment which has high noise immunity and excellent rejection of common
mode voltages. Common devices such as thermocouple and tachometer readouts
often "misbehave" and provide unreliable readings if they are not capable of
faithful operation in these high dV/dt conditions. This effect makes activities such
as drive start-up and troubleshooting difficult as specialized equipment is required
to take even basic measurements.
Noise
As discussed earlier, one source of acoustic noise is the air noise caused by
running shaft driven fans above their design speed to achieve a wider speed range.
A separately powered, unidirectional, constant speed cooling fan will provide a
consistent level of air noise independent of motor speed and eliminates annoying
sound level changes as the motor accelerates and decelerates.
A second source is the magnetic noise from flux harmonics which are driving the
magnetic core steel into a saturated condition. A well planned design will use
lower than nominal flux levels with particular emphasis on avoiding localized
regions of higher flux density or "pinch points". Air gap length and rotor slot
bridge thickness, which reduce saturation in localized areas are two contributing
areas where additional reductions in sound power level can be achieved.
72
reduce harmonic flux that contributes to parasitic torques. Also, the use of a
laminated frame construction eliminates a separate frame and stator structure
which simplifies the mechanical system and reduces the richness of possible noise
producing natural frequencies and modes of vibration. If a square frame
configuration is used it will tend to suppress odd ordered modes of vibration
which are present round bodied configurations. This is illustrated in Figure 9.
Figure 9
In summary, there are many factors that combine and ultimately result in noise at
the motor. The motor and controller must be considered as a system to insure the
desired results.
Mechanical Flexibility
One consideration is to achieve the maximum output from the smallest possible
motor. High performance adjustable frequency drives are often incorporated as
part of specialized machinery or processes where machine real estate is at a
premium. The standardization of NEMA fixed frequency dimensions creates
unnecessarily large motors and offers few alternatives. The practice of over sizing
the rating in order to achieve a speed range aggravates the problem. The
replacement of the inactive frame material of conventional AC induction motors
73
with active materials (conductors and magnetic steel) in a laminated frame
construction allows a larger air gap diameter and increased power density (Figure
10). Often up to two frame diameters can be reduced by using this technique.
Figure 10
Also, to take full advantage of the variable frequency controller the motor must be
capable of operating above its fixed frequency design speed at 60 Hz. The
standard motor design considers only acceleration up to and operation near its
synchronous speed. As a result few of these designs are expected to operate above
3600 RPM. The conventional AC motor rotor support to ground system (via
bolted joints to the frame, etc.) can give rise to a low stiffness-to-ground and to
second order modes of vibration (two level dynamic systems, as shown in Figure
11), which tend to reduce the value of the lowest critical speed. While all elements
of a high speed motor system (bearings, rotor balance and strength, etc.) must be
evaluated for suitability, the use of integral feet on the end brackets provides
increased stiffness to ground by eliminating one of the joints. This can result in
increased values of the lowest critical speed and permit operation at higher speeds.
Figure 11
Standard feet-on-frame design can result in a two
level dynamic system with lower operating speed
capability.
74
mounting flange but also combinations of brakes, speed feedback devices, and a
variety of cooling airflow methods and directions. The design must allow for these
devices to be accessed, removed and replaced in service with little difficulty.
Providing these features results in a design approach very similar to DC designs
and conflicts with much of the standardization in standard AC motors.
75