on cooldown for gas turbine
 

 Home  Forums  General Discussion  Power Generation

on cooldown for gas turbine


 PATR I A GIRI ·  Jun 14, 2011

Search Forums New Posts

Thread Starter #1
patria giri
P Jun 14, 2011

I wanted to ask about the turbine GE MS 9001E, after overhauling cooldown can not be done, when the torque
converter (voith) did not participate dismantled (not experiencing overhaul). as additional information, 1, 2, 3
turbine bearings replaced new with appropriate clearance standard. If using with hydraulic jack from the
compressor clutch to acc gear, turbine rotor can rotate but if using a torque converter (cooldown) only lasted
about 5 minutes. Is it possible to set the angle of transmission fluid in a torque converter? Please advice

 Like  Reply

CSA #2
Jun 15, 2011

This happens when new bearings are installed in the machine.

Cooldown, sometimes called "slowroll," through the Voith torque converter is VERY dependent on oil
temperature. It must be above approximately 27 deg C (approx. 80 deg F) to maintain slowroll.

It is also dependent on bearing clearances. You say they are as per spec, but there is usually a range, and if you
are on the low end of the range, then it might just be a little too tight.

It might also be very likely that the limit switches on the torque converter adjustor drive mechanism (presuming
it uses limit switches) may not be properly adjusted.

When this happens, it's usually required to run the machine at rate load for a few hours to get everything nice
and hot and start opening up the bearing clearances a little.

Fear not; it is NOT a controls problem. It just takes a little "run-in" time.

There is a manual handwheel on the torque converter which can be used to open the torque converter guide
vanes to port more oil to the torque converter "motor". You can try this temporarily, but after the machine is
warmed up and hot, everything should be okay.

 mnewiraq

 Like  Reply

patria giri #3

P Jun 16, 2011

thanks for the advice, after going through several experiments on cooldown ( about 100 times ) and
interspersed with wearing crankine motor (300 rpm, about 15 minutes), the turbine can operate (start unit ) with
a load of 90 MW, a bearing vibration: 3.5 mm / s, 2: 1.0 mm / s, 3: 7.5 mm / s, and operated by HSD for 24 hours.
Then do the shutdown to try if the process goes on cooldown, but it was on cooldown process failed. is there
any possible problems in the torque converter ( Voith )? Please advice to resolve

 Like  Reply

CSA #4
Jun 17, 2011

When the new bearings were installed in the GT, was an alignment of the bearing housings performed? (These
days, that's usually done with a laser-equipped device.)

Was the alignment of the generator to the turbine checked and adjusted after the new GT bearings were
installed?

Was the accessory gear alignment to the turbine checked and adjusted after the new GT bearings were
installed?

<b>You DID NOT reply with any information about the L.O. Header temperature (usually signal name LTTH, or
LTTH1). What is the L.O. Header Temperature when you trying to keep the unit on Cooldown via the torque
converter?</b>

Did you try using the manual handwheel on the Torque Adjustor mechanism when the unit is on Cooldown to
open the Torque Converter guide vanes more to see if it helps with the problem, which might indicate that the
Torque Adjustor limit switches might require adjustment?

(The above presumes that limit switches are used to position the Torque Converter guide vanes, and that some
other mechanism (like a position indicator or a current transducer) isn't used for controlling the torque
transmitted by the Torque Converter.)

You have said that the Torque Converter was refurbished during the outage. How was it "tested" or
commissioned during the re-start after the outage? It's entirely possible that it is not properly adjusted, but we
can't know that. There's no "detent" for slowroll that you can just make a simple adjustment to arrive at; it's a
field-adjusted variable.

Years ago we had a similar thread; please use the 'Search' feature in the far right corner of the Menu bar at the
top of every control.com page to find related threads. I don't recall exactly what the final outcome was.

I think the thread I was referring to is:

http://www.control.com/thread/1258018039

 Like  Reply

farid #5

F Jun 17, 2011

I have face the same problem as above. My machine was GE Frame 9E Rated 100MW. When put on TG after
crank the speed seem to be lower than actual TC setting of 110 turn..n then after fire for about 3 hours during
commissioning n then shutdown, TG motor was cut in but the shaft not rotate. it cause us to be put on standstill
for 48 hours. do u have any idea what are the cause of this problem?

 Like  Reply

mnewiraq #6
Sunday at 10:52 PM

Hi sir,
Do you remember what was the solution?
I've seen that you are posting new posts so i came back to the old thread.

 Like  Reply

You must log in or register to reply here.

Similar threads Forum Replies Date

Aero Gas Turbine trapped in cooldown


K Power Generation 2 Jun 13, 2020
during stop command

General
K Aero Gas Turbine in cooldown trap 0 Jun 13, 2020
Automation Chat

H Cooldown sequence Power Generation 0 Feb 28, 2020

GE Mark V Electronic Overspeed Test on


R Power Generation 2 Oct 12, 2019
Cooldown

E Cooldown Turbine Frame 5 Power Generation 2 Jan 22, 2019

Y O U M AY ALSO L IK E

ABB Upgrades Rockwell Yaskawa Adds New What is


Dormant Nordic Automation Compass So ware Redundancy in
Kra Pulp Mill in Releases New SIL 3 to IEC Control Systems?
Quebec With Safety Controller Environment for
Quality Line with Motion Control
Management Advanced So ware
System Capabilities
by Alessandro Mascellino by Alessandro Mascellino by Leah Scully by Muhammad Asim Niazi

WHO WE ARE PRODUCTS INDUSTRY CONTENT

Circuit Protection Agriculture Company Directory

Connectors Automotive Forums

Control Panel Building Industry White Papers

Control Systems & HMIs Cement News


More about us 
Enclosures, Racks & Cabinets Chemical Technical Articles

IIoT Electronics Textbook

Industrial Controls Food & Beverage Worksheets

CONNECT WITH US Motors Metal

Networking Military/Aerospace

    PLCs & PACs Mining

Pneumatics & Hydraulics Nuclear

Power Oil & Gas

Contact Us Advertise Protocols Medical & Pharmaceutical

Robotics Pulp & Paper


Write For Us Safety Rubber & Plastics

Sensors Utilities

Simulation View All

Test & Measurement


SIGN UP
Vision Systems

Wire & Cable


Enter your email address Register
View All

MORE FROM OUR NETWORK

    

© EETech Media, LLC. All rights reserved Privacy Policy · User Agreement

You might also like