Project report: Solaire Elevator ASD Project

System provider: Customer:


Company: Extinguished Inc Solaire Hotel Resort and Casino
Address: 14 Villa Soccoro St Proj 8 Quezon City Tambo Entertainment City, 1 Asean Ave, Tambo Paranaque City
1709
Town:
Phone:

Comment:
Sky Forum Elevator 7-8

EN 54-20 class EN 54-20 compliant possible reasons


C Yes
B Yes
A Yes

Project name: Solaire Elevator ASD Project


Project build date: 12/08/2020 14:48:05
Fan level: III
Ambient temperature [°C] 20
Ambient pressure [hPa] 950,0

Tube network I Tube network II


Maximum smoke sensor sensitivity according EN 54-20 class C 1,553 --
Maximum smoke sensor sensitivity according EN 54-20 class B 0,270 --
Maximum smoke sensor sensitivity according EN 54-20 class A 0,092 --
Maximum transport time [s] 54 --
Overall sampling tube length [ m ] 20,50 --
Number of sampling points 3 --

SKY TOWER FORUM 7-8.report.pdf / 06/01/2021 21:32:42 / ASD PipeFlow 2.7.0.7 - Page 1-
Sketch of tube network:

E:\SOLAIRE PIPEFLOW\SKY TOWER FORUM 7-8.report.gif

SKY TOWER FORUM 7-8.report.pdf / 06/01/2021 21:32:42 / ASD PipeFlow 2.7.0.7 - Page 2-
Part Description RL TL S[C] S[B] S[A] P Fl ø t L-cap SP-cap Comment:
(ASD) ASD 535 0,00 0,20 0
A1 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 0,20 0,20 258 0,20 0
stainless steel)
A2 (AN 25-90 PVC) Angle 90° D=25 mm PVC 0,20
A3 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 0,30 0,50
stainless steel)
A4 (AN 25-90 PVC) Angle 90° D=25 mm PVC 0,50
A5 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 0,20 0,70
stainless steel)
A6 (DFU 535L) Dust Filter Unit large D=25 mm 1,20
A7 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 2,20 3,40
stainless steel)
A8 (AN 25-90 PVC) Angle 90° D=25 mm PVC 3,40
A9 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 0,20 3,60
stainless steel)
A10 (AN 25-90 PVC) Angle 90° D=25 mm PVC 3,60
A11 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 2,90 6,50
stainless steel)
A12 (AN 25-90 PVC) Angle 90° D=25 mm PVC 6,50
A13 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 0,40 6,90
stainless steel)
A14 (AN 25-90 PVC) Angle 90° D=25 mm PVC 6,90
A15 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 0,50 7,40
stainless steel)
A16 (AN 25-90 PVC) Angle 90° D=25 mm PVC 7,40
A17 (TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, 13,10 20,50
stainless steel)
A17 - 1 -1- Sampling point / Clip 0,20 7,60 6,640 1,150 0,390 252 0,07 2,00 14
A17 - 2 -2- Sampling point / Clip 6,35 13,95 6,660 1,160 0,400 250 0,07 2,00 28
A17 - 3 -3- Sampling point / Clip 6,35 20,30 6,670 1,160 0,400 250 0,07 2,50 54
RL: Relative length of this part (distance to previous SP or bend) [m]
TL: Total length of the part end to the ASD [m]
S[C]: Smoke sensitivity [%/m] for this sampling hole, when the smoke sensor alarm level is chosen as proposed in this report.
S[B]: Smoke sensitivity [%/m] for this sampling hole, when the smoke sensor alarm level is chosen as proposed in this report.
S[A]: Smoke sensitivity [%/m] for this sampling hole, when the smoke sensor alarm level is chosen as proposed in this report.
P: Pressure [Pa]
Fl: Airflow [Liter/s] of this sampling point
ø: Diameter [mm]
t: Transport time to the ASD [s]
L-cap: Length of the capillary / stub [ m ]
SP-cap: Samplingpoint of the capillary

SKY TOWER FORUM 7-8.report.pdf / 06/01/2021 21:32:42 / ASD PipeFlow 2.7.0.7 - Page 3-
Material list:
Part Number Length [ m ] Rod length [ m ] Number of rods Comment:
(ASD) ASD 535 1
(TU ID 19) Sampling tube ID=19 mm (e.g. Cu, aluminium, stainless steel) 9 20,00 5,00 4
(AN 25-90 PVC) Angle 90° D=25 mm PVC 7
(DFU 535L) Dust Filter Unit large D=25 mm 1
(CLIP 2.0 PA) Sampling hole clip d=2.0 mm red PA 2
(CLIP 2.5 PA) Sampling hole clip d=2.5 mm red PA 1
(PC 25 PP) Pipe clamp type Goema halogen-free 21

SKY TOWER FORUM 7-8.report.pdf / 06/01/2021 21:32:42 / ASD PipeFlow 2.7.0.7 - Page 4-