Learning Outcomes
Upon successful completion of this session, you will be able to:
• Recall the hybrid 2 port model of the transmission line
relating the voltages and currents at the sending and
receiving ends in terms of A, B, C & D constants.
IS IR
A B
VS VR
C D
Figure 1: Two-port Model of a Line
B = ZC sinh ( γl) Z
⎛ ZY ⎞
C = YC sinh ( γl) Y⎜ 1 + ⎟
⎝ 4 ⎠
Here Z = zl Ω and Y = yl S
z y
γ = zy ZC = YC =
y z
⎡ VS ⎤ ⎡ A B⎤ ⎡ VR ⎤
⎢ ⎥=⎢ ⎥ ⎢ ⎥
⎢ ⎥ ⎢ ⎥ ⎢ ⎥
⎢⎣ IS ⎥⎦ ⎢⎣ C D⎥⎦ ⎢⎣ IR ⎥⎦
A, B, C, D -are called generalised line constants.
γ = zy = α + jβ = j LC .ω i. e. α = 0 and β = LC .ω
B = zl
sinh( γl)
= jLωl
sinh( jβl) j sinh(βl) Lω
= = j
(
sinh LCωl Lω )
γl jβl β ω LC
B=
L
C
( )
sinh ωl LC ∠ 900 ≈ Lωl∠ 900 for small βl.
Activity 4A
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Calculate the active and reactive power at the receiving end
of the transmission line from the voltage-current equations.
δ is the angle between the receiving end and the sending end
voltages and is called the load angle or power angle.
VS AVR
IR = ∠δ − β − ∠α − β (3)
B B
VS AVR
I*R = ∠( β − δ ) − ∠ ( β − α ) and S R = VR I*R = PR + jQ R
B B
V V AVR2
∴ SR = R S ∠(β − δ ) − ∠(β − α ) (5)
B B
V V AV 2
PR = R S cos(β − δ) − BR cos(β − α) (6)
B
V V AVR 2
Q R = R S sin(β − δ) − sin(β − α) (7)
B B
Activity 4B
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Describe the conditions that affect the power carrying
capability of a transmission line and calculate the practical
power carrying capability.
In long lines, the power transfer limit is reached well before the
thermal limit of the conductors is reached. In this case the power
transfer capability is determined by the line constants rather
than the current carrying capacity of the conductors.
Activity 4C
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Derive the voltage and current relationships in a lossless line.
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Calculate the wavelength.
1
or λf = = velocity of electromagnetic wave
LC
1
For overhead lines C0 = ≈ 3 × 108 m / s
LC
3 × 108
f = 50 H Z → λ= ≈ 6000 km
50
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Describe the effect of surge impedance loading at the
receiving on the sending end active & reactive powers.
IS IR
VS Vx VR RL = Z0
SE RE
x
If VR = VR ∠00 Vx = VR ∠β x (9)
That is the magnitude of V along the line is the same; but there is
a phase shift of β radians per metre length. Thus at the SE where
x= l VS = VR ∠β l .
VS = VR = Vrated
V 2 (V ) 2
PR = R = rated & QR = 0 (10)
RL Z0
P S = PR & QS = 0
Activity 4D
Tutorial Problem
A 500 kV line has a surge impedance of 350 Ω. Calculate
the surge impedance loading of the line.
Answer to this problem is provided at the end of Part C
Session 4.7
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Describe the effect of open circuit on the receiving end
voltage.
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Derive the equations for the voltage and current at any point
on a line when the RE of the line is terminated by a general
impedance ZR. Calculate the forward and backward voltage
components at the sending end.
• Calculate the forward and backward voltage components
when the load at the receiving end is an open circuit. Use
these components to calculate the voltage profile along the
line.
• Calculate the forward and backward voltage components
when the load at the receiving end is on short circuit. Use
these components to calculate the voltage profile along the
line.
• Calculate the forward and backward voltage components
when the load at the receiving end is the characteristic
impedance. Use these components to calculate the voltage
profile along the line.
• Calculate the reactive power compensation required at the
receiving end.
VS Vx VR ZR
SE RE
x
( )
(11)
I x = YC VfS e− γx − VbS eγx
VR
VS = AVR + BIR but IR =
ZR
Let us express VR and IS in terms of VS
VS
∴VR = (13)
A + B / ZR
07-11-2003 Rev 1.0
⎛ A ⎞
IS = CVR + AIR = ⎜ C + ⎟ VR (14)
⎝ ZR ⎠
⎛ A + CZ R ⎞
IS = ⎜ ⎟ VS (15)
⎝ B + AZ R ⎠
⎡ Z ( A + CZ R ) ⎤ VS
VfS = ⎢1 + C ⎥
⎣ (B + AZ R ) ⎦ 2
Thus, (16)
⎡ Z ( A + CZ R ) ⎤ VS
VbS = ⎢1 − C ⎥
⎣ (B + AZ R ) ⎦ 2
Vx = VfS e − γx + VbSe γx
( )
and
Ix = YC VfS e − γx − VbS e γx
⎛ Z C⎞ V ⎛ Z C⎞ V
VfS = ⎜ 1 + C ⎟ s and VbS = ⎜ 1 − C ⎟ s (17)
⎝ A ⎠ 2 ⎝ A ⎠ 2
⎛ Z A⎞ V ⎛ Z A⎞ V
VfS = ⎜ 1 + C ⎟ s and VbS = ⎜ 1 − C ⎟ s (18)
⎝ B ⎠ 2 ⎝ B ⎠ 2
V V
VfS = (1 + 1) s = Vs and VbS = (1 − 1) s = 0 19)
2 2
Activity 4E
Voltage Profile
Consider a 400 km long 500 kV line whose series impedance
is (0.030+j0.300) Ω/km and shunt susceptance is 3.65
µS/km. For this line:
γ = zy = 5.23x10−5 + j1.05 x10−3
α = 5.23x10−5 nepers/km β = 1.05 x10−3 radians/km
Characteristic impedance,
Z C = z / y = 287.05 − j14.32 = 287.41∠ − 2.86o Ω
A = D = 0.9137+j0.0085= 0.9137∠0.530
B = 11.31+j116.56 = 117.11∠84.460 Ω
C = -4.190E-6+j1.418E-3 = 0.0014∠90.170 S
The sending end voltage is held at 500 kV.
Obtain the voltage profile of the line when the receiving end
is
1. Open Circuited,
07-11-2003 Rev 1.0
2. Short Circuited,
3. Terminated by the Characteristic Impedance of the
line and
4. A load of 303.17∠14.04o Ω ,
( That is a load of 652.1 MW and 163.0 MVAr lagging at 500
kV).
Activity 4F
Voltage Profile
A 765 kV line has the following constants.
A = D = 0.9313∠0.2090
B = 97.0∠88.60 Ω
Characteristic impedance, ZC = 266.1Ω∠0o .
Calculate
Learning Outcomes
Upon successful completion of this session, you will be able to:
• Derive the receiving end voltage in terms of the fixed SE
voltage and the apparent power at the receiving end.
• Use the equation to calculate the voltage at RE for various RE
power at a fixed power factor. Identify the maximum power
at which the voltage collapse begins.
VS = AVR + BI R
In this equation all the quantities are phasors and in our usual
manner let us represent the phasors by the following polar
forms, taking VR as the reference phasor:
P − jQ R
IR = R (20)
VR
Substituting (20) into the equation for VS,
P − jQ R
VS = AVR + B R (21)
VR
In terms of the real magnitudes and angles, (21) becomes
VR VS (cos δ + j sin δ ) =
[ AVR2 cos α + B(PR cos β + QR sin β)] + j[ AVR2 sin α + B(PR sin β − QR cos β)]
(23)
[
VR VS (cos δ + j sin δ ) = AVR ] [
2 cos α + K + j AV 2 sin α + K
P R Q ] (24)
( ) (
VS2 VR2 = A 2 VR4 + 2 A K P cos α + K Q sin α VR2 + K 2P + K Q
2
) (25)
K 2P + K Q
2
( )
= B2 PR2 + Q 2R = B2S2R (26)
(
S2R = PR2 + Q 2R ) (27)
Since (27) is in a quadratic form of VR2 , the solution for VR2 can
easily be obtained using the well known formula.
[ (
b = VS2 − 2 A K P cos α + K Q sin α )] (29)
1 ⎧
b ± b 2 − ( 2 ABSR ) ⎫⎬
2
VR2 = 2⎨
(30)
2A ⎩ ⎭
1 ⎧
b ± b 2 − ( 2 ABSR ) ⎫⎬
2
VR = 2⎨
(31)
2A ⎩ ⎭
Activity 4K
Power transfer
Consider the 400 km long 500 kV line whose A & B
constants are:
A = 0.9137∠0.53o and B = 117.11∠84.46o Ω.
Review problems
Power Transfer
Answers are provided within parenthesis.
1. The A, B, C & D constants of a 132 kV transmission line
are:
A = D = 0.936 ∠1.0o,
B = 141.4 ∠83.1o Ω,
C = 0.906∠83.1o mS
The characteristic impedance of the line at 50 Hz is 395.0
Ω.
Calculate
(a) the surge impedance loading of the line.
(Ans: 44.1 MW)